Remeha Boiler/CV - logging data from serial port to ESP8266
rjblake
Post by rjblake » Tuesday 13 December 2016 12:22
I have a Remeha Calenta 40C and the built in serial port provides plenty of information on the boiler operations. I have built and installed the excellent Opentherm gateway and happily getting some information from it to manage my heating system. But, as always - I want more! Looking at the Remeha Recom software, there are a number of really useful additions to the standard Opentherm messages that would make it even better. Add the ability to plug in an ESP8266 directly to the boiler and you have an excellent management addition to your system. So far, I've managed to sniff the correct HEX string to poll the boiler for data and receive a response. Looking to create a LUA script to do this, but at a loss as to how to get this into Domoticz. Would I need to create a PR and look to add new 'Remeha' hardware which could/would be configured based on the model (Avanta, Calenta, Tzerra, etc. - although there are more sub models/versions per the Recom XML files)? Anybody been down this route or have any interest?
rjblake
Re: Remeha Boiler/CV - logging data from serial port to ESP8266
Post by rjblake » Sunday 08 January 2017 19:05
Quick update - having found some others (Robert Hekkers & Peter Maaswinkel) who had done similar elsewhere, I've managed to create/adapt/update a PHP script that connects to the ESP8266 and receives/decodes the information correctly from the Remeha Calenta 40C (results will vary by model). Have now added code to populate devices in Domoticz and all working correctly. CRC check has also been added. Total cost of €12.00 for hardware which gives me more options than my OTGW :)
For those who want the code as it stands, I have now added this to GitHub https://github.com/rjblake/remeha
Have made a few updates and now can decipher the following:
1. Identification
2. Configuration Parameters (I have not enabled the update as have not sorted the CRC checks/validation and a bit risky if wrong data is sent)
3. Samples
4. Counters
Some sample runs of the PHP scripts on my boiler as below:
IDENTIFICATION
PHP version: 7.0.21
Connected to XXX.XXX.XXX.XXX:YY
Sending request...
ID-01 read: 0200FE0648010B0A0D01FFFF191205040002FFFFFFFFFF0403FF01FFFFFFFFFFFFFFFFFFFFFFFF3134333131313032393932323020202043616C656E7461202020202020202020D92603
ID-02 read: 0201FE0618010B03191205320A0104160EE614424D08923E4B03
ID-03 read: 0203FE0618010B011523010C960304020E2C1437502855278103
Identification used: 0200FE0648010B0A0D01FFFF191205040002FFFFFFFFFF0403FF01FFFFFFFFFFFFFFFFFFFFFFFF3134333131313032393932323020202043616C656E746120202020202020202003191205320A0104160EE614424D0892011523010C960304020E2C1437502855
Data Integrity Good - CRCs Compute OK
Identification Information Received: 2017-11-02 10:16:23
Boiler Name: Calenta
dF-Code: 13
dU-Code: 1
Boiler Serial Number: 1232220299234
Software Version: 1.9
Parameter Version: 1.2
Parameter Type: 5
Next Service Type: A
PCU Device Type: 3
PCU Serial Number: 1442M0298
PCU Software Version: 1.9
PCU Parameter Version: 1.2
PCU Parameter Type: 5
PCU Operating Hours: 25620
PCU Connected SU Type: 1
PCU Connected PSU Type: 4
PCU Last Blocking Code: 22
PCU Last Locking Code: 14
Operating Voltage: 230 volts
SU Device Type: 1
SU Serial Number: 3714P2855
SU Software Version: 1.5
SU Parameter Version: 2.3
SU Parameter Type: 1
SU Operating Hours: 25776
SU Connected PCU Type: 3
SU Connected PSU Type: 4
SU Last Blocking Code: 2
SU Last Locking Code: 14
SU Last Internal Error: 44
PARAMETERS
PHP version: 7.0.21
Sending request...
Param-01 read: 0200FE061810143C37010100020501FFFFFFFFFFFFFFFF862403
Param-02 read: 0200FE061810152A44114B28085AFF1414F10206F601143FF603
Param-03 read: 0200FE06181016040000010100000100000001AF1E23FFC10C03
Param-04 read: 0200FE06181017FFFFFFFFFFFFFFFFFFFFC80200232C36004403
Param-05 read: 0200FE061810180128465A3219051E0A1E030944442814BC4303
Param-06 read: 0200FE061810195039075405000F02050632190001B309523403
Param-07 read: 0200FE0618101A0078640A061E284B00FE0A000A640228227F03
Param-08 read: 0200FE0618101B1A010A05021428141E7A0A00FF000C1AE4CD03
Parameters used: 0200FE061810143C37010100020501FFFFFFFFFFFFFFFF2A44114B28085AFF1414F10206F60114040000010100000100000001AF1E23FFFFFFFFFFFFFFFFFFFFFFC80200232C360128465A3219051E0A1E0309444428145039075405000F02050632190001B3090078640A061E284B00FE0A000A6402281A010A05021428141E7A0A00FF000C1A
Parameters Received: 2017-11-02 10:15:46
Max. Flow Temp. during CH mode: 60°C
Desired DHW temperature: 55°C
Switch On/Off CH/DHW Functions: 1
DHW Comfort Setting: 1:Always Off
Anticipation curent On/Off Thermostat: 0:No
Amount of Information to Display: 2:Automatic
Pump post run time: 5 minutes
Display Brightness: 1:High
Max Fanspeed during CH mode: 4200 rpm
Max Fanspeed during DHW mode: 6800 rpm
Max Fanspeed during CH+DHW mode: 1700 rpm
Offset on part load fanspeed: 75 rpm
Fanspeed at boiler start: 4000 rpm
Min. water pressure for notification: 0.8 bar
Max Flow temperature for CH: 90°C
Footpoint heating curve outside temperature: 20°C
Footpoint heating curve flow temperature: 20°C
Clima P outside temperature: -15°C
Pump Control - CH minimum speed: 20 %
Pump Control - CH maximum speed: 60 %
Minimum outside temperature for Frost Protection: -10°C
Anti-Legionella setting: 1:Yes
Setpoint raise at warming up of calorifier: 20°C
Switch on hysteresis calorifier sensor: 4°C
Three-way valve standby position: 0:CH
Boiler Type: 0:Combi
Blocking Input: 1:Blocking without Frost Protection
Release Input: 1:Burner Release
Release Wait time: 0 seconds
Fluegas valve Wait time: 0 seconds
Status Report: 1:Failure signal
Minimum Gas Pressure Detection: 0:No
HRU Connected: 0:No
Mains Live-Neutral phase Detection: 0:No
Service Notification for Boiler Dependent Maintenance: 1:ABC
Service Hours for Boiler connected to mains: 17500
Service Hours for Boiler Burner: 3000
Tau Factor for average flow temperature calculation: 35 seconds
DHW-in gradient for restart stabilisation time: 2°C/second
dT pump offset: 2°C
Offset Control temperature: 0°C
DHW Flow at minimum output power: 3.5 litres/minute
Number of de-airation cycles on startup: 1
Maximum gradient for decreasing modulation: 0.4
Maximum gradient for forced minimal load: 0.7
Maximum gradient for blocking: 0.9
Maximum temp difference between flow and return: 50°C
Modulate back when dT > this parameter: 25°C
Pump control, control range dT for CH: 5°C
Pump control, CH on start heatdemand: 30 %
Start hysteresis for CH: 10°C
Stabilisation time after burner start CH: 30 seconds
Minimum burner anti-cycle time: 3 minutes
Maximum burner anti-cycle time: 9 minutes
Absolute max fan speed CH: 6800 rpm
Absolute max fan speed DHW: 6800 rpm
Pump control, control range dT for DHW: 40°C
Pump control, DHW minimum speed: 20 %
Pump control, DHW maximum speed: 80 %
Pump control, DHW on start DHW demand: 57 %
Warm up interval for DHW after CH: 7 minutes
Time between warming up starts boiler: 84 minutes
Hysteresis when warming up for DHW comfort: 5°C
Offset when warming up for DHW comfort: 0°C
DHW start raise depending op DHW flow: 15
Switch on hysteresis DHW operation: 2°C
Offset DHW: 5°C
Temperature correction DHW for Tset, ww - Tret, plate heat exchanger: 6°C
%Tf/Tr for DHW control temperature at pumpspeed 20%: 50 %
%Tf/Tr for DHW control temperature at pumpspeed 100%: 25 %
Waiting time pump for preheat plate heat exchanger: 0 seconds
Postpump time DHW: 1 seconds
Correction factor DHW pulses to litres/minute: 179
Minimum DHW flow for DHW detection: 0.9 litres/minute
Type of Sensor for DHW detection: 0:DHW Flow Sensor
Factor for dynamic flow detection: 120
DHW stabilisation time for pump modulation: 10 seconds
DHW gradient for stabilisation time pump: 0.1°C/second
Range in which the DHW booster is diabled: 6°C
P factor for booster on start DHW: 30
P factor for feedforward on flow DHW: 40
P factor for booster on flowchanges DHW: 75
Switch off offset calorifier sensor: 0°C
Switch on delay DHW pump in comparison with boiler pump: -2°C
Post pump time DHW: 10 seconds
Prepurge time for burner start: 0 seconds
Postpurge time for burner stop: 10 seconds
Maximum flow temperature for blocking: 100°C
Tacho pulses per revolution of the fan: 2 /second
P factor fan speed contro: 40
I factor fan speed contro: 26
P factor CH control: 1
I factor CH control: 10
P factor for CH control when T1>setpoint: 5
I factor for CH control when T1>setpoint: 2
P factor DHW control: 20
I factor DHW control: 40
I factor for pump control on CH: 20
I factor for pump control on DHW: 30
RPM at theoretical 0KW: 122
Power output (KW) at theoretical 10,000rpm: 10 KW
PWM value red for normal display backlight: 0
PWM value green for normal display backlight: 0
PWM value blue for normal display backlight: 255
SAMPLES
PHP version: 7.0.21
Sending request...
Sample Data read: 0201FE064802013C0F240F0080008080F300801211D607BC027C15D0070000000000BC020000000000000001C20B1000FFFF00000000FFFF1100BC020000000080000000000000CE9503
Sample Data Received: 2017-11-02 10:15:15
Flow Temperature: 39.00°C
Return Temperature: 38.76°C
DHW-in Temperature: Open
Calorifier Temperature: Open
Outside Temperature: Open
Control Temperature: 7.00°C
Internal Setpoint: 7.00°C
CH Setpoint: 7.00°C
DHW Setpoint: 55.00°C
Room Temperature: 20.06°C
Room Temp. Setpoint: 20.00°C
Boiler Control Temperature: 43.70°C
Solar Temperature: Open
Fan Speed setpoint: 0rpm
Fan Speed: 0rpm
Ionisation Current: 0.0μA
Pump Speed: 0%
Hydro Pressure: 1.7bar
DHW Flow rate: 0.00litres/minute
Desired Max.Power from controller: 0%
Output: 0%
Actual Power from boiler: 0%
Valve Flags: 00001011
Gas Valve[0]: 1:Closed
Ignition[2]: 0:Off
3-Way Valve[3]: 1:DHW
External 3-Way Valve[4]: 0:Open
External Gas Valve[6]: 0:Open
Pump Flags: 00010000
Pump[0]: 0:Off
Calorifier Pump[1]: 0:Open
External CH Pump[2]: 0:Off
Status Report[4]: 1:Closed
Opentherm Smart Power[7]: 0:Off
Input Flags: 11000010
Shut down Input[0]: 0:Closed
Release Input[1]: 1:Open
Ionisation[2]: 0:No
Flow Switch Detecting DHW[3]: 0:Open
Minimum Gas Pressure[5]: 0:Open
CH Enable[6]: 1:Yes
DHW Enable[7]: 1:Yes
Heat Request Flags: 00000001
Mod.controller Connected[0]: 1:Yes
Heat Demand from Modulating Controller[1]: 0:No
Heat Demand from ON/OFF controller[2]: 0:No
Heat Demand from Frost Protection[3]: 0:No
DHW Eco[4]: 0:Yes
DHW Blocking[5]: 0:No
Heat Demand from Anti Legionella[6]: 0:No
Heat Demand from DHW[7]: 0:No
HRU Flags: 00000000
HRU Active: 0:Open
Combined State/Sub-State: 0:Standby/0:Standby
Lockout/Blocking: No Locking/No Blocking
Boiler fault: False
Flame is: Off - Off - Off
Last Update:2017-11-02 10:13:19 Time Now:2017-11-02 10:15:15 Elapsed:1.93
Update Changes Only: Domoticz Update:1 Update All:0
COUNTERS
PHP version: 7.0.21
Sending request...
Counter Data-1 read: 0200FE0618101C04652E3F03660061320A01AD01470CE61E9C03
Counter Data-2 read: 0200FE0618101D0DFC00040002000000000000000000005E6503
Counter Data-3 read: 0200FE0618101E00000000000000000000000000000000937D03
Counter Data-4 read: 0200FE0618101F00000000000000000000000000000000C2ED03
Counters Received: 2017-11-02 10:14:34
Hours run pump CH+DHW: 2250 hours
Hours run 3-way valve DHW: 23678 hours
Hours run CH+DHW: 1740 hours
Hours run DHW: 97 hours
Power Supply available hours: 25620 hours
Pump starts CH+DHW: 3432 starts
Number of 3-way valve cycles: 2616 cycles
Burner Starts DHW: 26416 starts
Total Burner Starts CH+DHW: 28640 starts
Failed burner starts: 4 starts
Number of flame loss: 2 times
Last Update:2017-11-02 10:00:35 Time Now:2017-11-02 10:14:34 Elapsed:13.98
Last edited by rjblake on Thursday 02 November 2017 11:30, edited 1 time in total.
knny
Target OS: Raspberry Pi
Post by knny » Tuesday 31 January 2017 17:54
How to get this working in Domoticz?
I have a Remeha Tzerra with working FTDI cable and a raspberry Pi with Domoticz
rjblake
Post by rjblake » Tuesday 31 January 2017 19:54
knny wrote:How to get this working in Domoticz?
The PHP is written to communicate using the telnet port on the ESP. You'd need to change the code to work over USB. I'm not sure if the hex codes are the same for the Tzerra as they are for the Calenta, but you can try the PHP scripts (on github) I created. You need PHP on the Pi to run them. Best is to run the Recom software first to check the hex being sent to the Tzerra, check whick Recom XML file it is using and you may need to do some mapping. The quickest check is to run the remeha.php (php -f remeha.php) from a terminal window after you have edited the .ini file with your IP address etc.
knny
Post by knny » Wednesday 01 February 2017 22:26
I'm not a programmer, so I have to wait till someone writes a script working for al Remeha's to work with Domoticz :roll:
rjblake
Post by rjblake » Wednesday 01 February 2017 23:10
It will be difficult/near to impossible to do without have a Tzerra to test this with unfortunately as Remeha does not publish the technical documentation required to communicate with the CV. Only through sniffing the packets to/from the CV is this possible. Once certain parameters are known, it is a matter of mapping these to some XML files (that are readily available from the Remeha Recom software) to decode the information into something that can be translated for Domoticz or other purposes. As suggested, you should try this with at least the Recom software or simply run the existing scripts. If you get responses from the scripts, it is a good start. A better position to be in after this is to know what XML file matches your CV - that way the scripts can easily be modified to suit your specific model CV. Also, using an ESP8266 plugged directly into the CV would mean that no rewrite is needed for the Telnet vs. USB communications and you can buy these for between €5-12 so a cheap option
knny
Post by knny » Thursday 02 February 2017 9:53
OK, I have a working FTDI rj10 to usb cable right now. It is recognised in Recom software so that's running fine.
I have found a ESP8266 module with USB port already included. I assume that my rj10 to USB cable gives it his power then.
This is the device https://www.kiwi-electronics.nl/adafrui ... p8266-wifi
With that I can try to run the php files you made?
rjblake
Post by rjblake » Thursday 02 February 2017 21:08
Nope - wrong ESP - you'll want this one: https://www.kiwi-electronics.nl/adafrui ... ruit%20esp. You'll need an RJ10 cable to connect to the ESP8266, suggest loading it with the ESP-Link software (you'll need and FTDI cable /FTDI friend to do this) and from there you should be fine (see here http://domoticz.com/forum/viewtopic.php ... it#p107074. With the Recom software running and connecting to the CV, what does it say in the lower right corner? This is the same name as the XML file, which will give me some clues as to the format of the responses at least
Pvhpsb
Post by Pvhpsb » Wednesday 02 August 2017 15:58
I also started this project, but when I start remeha.php, I get data back with crc errors
When I work with Recom, I get the message Pcu-05 (P3)
Someone may have a tip?
Regards,
Patrick
rjblake
Post by rjblake » Thursday 21 September 2017 19:02
Patrick - what model Remeha do you have?
Ignore - forgot you'd sent a PM about your Tzerra
barak
Post by barak » Saturday 11 November 2017 10:12
@rjblake
first of all my english is bad but i hope you understand me :)
i can't write pm because of my new membership here :(
I try to copy your awesome work with ESP8266 Connection to remeha on github. (Connect ESP8266 directly to Remeha CV/Boiler to read data using PHP)
The Adafruit HUZZAH ESP8266 is flashed but my remeha is not a calenta, it is a AvantaComfort. Recom Software shows "Avanta Comfort V1(P2)".
my question: where do you find the hex codes transmit to remeha in remeha.ini under [Remeha Settings] ?
thank you very much for your hard work!
regards
Adam
I have posted this
rjblake
Post by rjblake » Thursday 16 November 2017 16:41
@rjblake
regards
Adam
I have posted this
Adam - I've sent you an email to the question from GitHub. the HEX codes to send for the various functions are in the INI file under the [Remeha Settings] section. I do not know these for the Avanta Comfort, so you will have to do some sniffing on the serial port while using Recom to see what they are for the various functions (Identification, Samples, Counters, Parameters) and also edit the various PHP files to match the responses with the XML file for the V1(P2) model.
barak
Post by barak » Thursday 16 November 2017 21:57
thx, i will try to sniff some hex codes but i think i am not able to understand the answer (even with the xml file)...
bgitmans
Target OS: OS X
Domoticz version: 3.5166
Post by bgitmans » Sunday 21 January 2018 21:54
I have also an Remeha Tzerra boiler, and I want to connect it to Domoticz as well.
I already found that the Tzerra is a PCU-05_P3 machine as defined in the xml files of RECOM.
However now I would need some help with the reverse engineering of the work already done for the Calenta.
I will start with using Wireshark to log the communication between RECOM and the boiler.